I have a functioning Heart Interface 2500 in my 1995 Unihome 280.  I have just replaced four dead GC2 6V batteries (PO had allowed them to freeze, and they literally broke open and spilled out the acid), with 4 new 6V AGM GC2 batteries.  The Heart Interface manual looks like it should be able to charge these correctly, but the is no de-sulfation cycle.

In the experience of the people on this forum,  would it be wise to replace the Heart Interface with something else now that I have new AGM batteries in place? 

Thanks

Mark
1994 U280 Grandvilla, 40ft.
League CIty TX
Newbie :-)

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #1
You are fine with that inverter/charger on AGM batteries.  If no AGM setting, set them to WET CELL.  The charging algorithms are very close.
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #2
Your inverter is pre seial  number 100,000 like our oem 97's.

No battery temp system.  The charging voltage is highly temp regulated.

All coaches past our Feb 97 build to this day have a battery temp controlled charging voltage.

Cold weather can get the correct voltage below mid 13's.  You are outputting over 14 unless you manually reset the voltage constantly.

No non lifeline brand AGM can be equalized. 

Electronic desulfurization does work I understand.

So we bit the bullet and had a magnum ms2812 and it's control panel and it's BTMS installed.

Fully charged batteries are good to minus 32 F. 

The overcharging may have blown up your previous batteries?

Or trying to equalize them to replace lost capacity?

Every new unicoach coach built for the last 20 years had a BTMS and mk gels new
"Riding and rejoicing"
Bob
1997 U320 40' Mid entry, build 5132,  wtbi ce27, 4th owner
2007 Solara convertible
2 prodeco tech outlaw ss electric bikes

1095 watts solar
08 Ls 460 and a sc430
2000 Ford F-250 superduty 4x4

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #3
Mark,

Does your inverter/charger not have a "cold vs hot ambient temperature" in its programming (along with type of battery and size of battery bank in amp-hrs?
Brett Wolfe
EX: 1993 U240
Moderator, ForeForum 2001-
Moderator Diesel RV Club 2002-
Moderator, FMCA Forum 2009-2020
Chairman FMCA Technical Advisory Committee 2011-2020

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #4
If I was going to upgrade and considering going with solar, this would be my choice.  Magnum Energy MSH3012M MSH-Series 3000W 12VDC Pure Sine Hybrid Inverter!  However, they are proud of these for sure!  I had the Magnum 2800 in our 5th wheel and it sure did do the job with 4- 6 volt AGM's.
Joe & Dottie Allen
Sold!  December 2023.      2000 U320; build # 5645
Our coach " Maxine"
Motorcade #  15922;  Escapee 150950; FMCA F330833; Boondockers Welcome;  Harvest Hosts;  Thousand Trails
'98 U320 from 2000-'06
USAF '62-'66

"Do not spoil what you have by desiring what you have not; remember that what you now have was once among the things you only hoped for." ―Epicurus

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #5
Your Heart unit is about 25 years old, you are living on borrowed time.
1995 U320C SE 40'
Jeep 4x4 Commander - Limited - Hemi
"The Pack"  Yogi and Diesel our Airedales -  Charlie our Boxer/Akita mix. Gone but NEVER forgotten Jake our yellow Lab.
NRA Law Enforcement Firearms instructor - Handgun/shotgun
Regional Firearms instructor for national Armored Transp. Co.

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #6
Good morning and Happy New Year to everyone on this forum!

I have a functioning Heart Interface 2500 in my 1995 Unihome 280.  I have just replaced four dead GC2 6V batteries (PO had allowed them to freeze, and they literally broke open and spilled out the acid), with 4 new 6V AGM GC2 batteries.  The Heart Interface manual looks like it should be able to charge these correctly, but the is no de-sulfation cycle
Some AGMs like ours, specifically warn against using a de-sulfation cycle. Our Heart is still working fine.

Pierce                   
Pierce and Gaylie Stewart
'93 U300/36 WTBI
Detroit 6V-92TA Jake
1140 watts on the roof
SBFD (ret)

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #7
The over and undercharging constantly from not having the chargers cycling and voltage set to match the batteries temp will have them lose capacity much faster than the correct voltages.  Which is why even less expensive inverter/chargers now offer a BTMS.  Read the heart freedom manual on line.  It mentions changing the chargers voltage manually to match the batteries temp. 
"Riding and rejoicing"
Bob
1997 U320 40' Mid entry, build 5132,  wtbi ce27, 4th owner
2007 Solara convertible
2 prodeco tech outlaw ss electric bikes

1095 watts solar
08 Ls 460 and a sc430
2000 Ford F-250 superduty 4x4

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #8
My opinion. . .

Replace it now. Take time to figure out what to replace it with and consider it a do it yourself learning project.

And do it when you have time and place, not 'on the side of the road'.

It will fail, quite old, not true-sine wave, lots of overheated components, limited flexibility.

Spend now when you will have many years enjoying your replacement.

And it may be friendlier to your new batteries. But even with your old batteries, the Heart should have been replaced.

Heart was a very good unit and may work for a long time. We had your Heart, and when it failed for what ever reason, it was in a campground.

If you decide to replace the heart, don't cut the heavy battery cables.

Disconnect the ground and positive cables at the battery.

Place Heart on work surface and open it up, which may/will destroy the Heart.

Find the bolts that attach the charger's internal end of the cable's big brass terminal.

Remove bolts and reuse cables with new chargers that all have external bolt connections.

Also just unplug the telephone-type RJ-11 remote panel cable, as it can be re-plugged into most new chargers.

If you go with Magnum, get the better of two remote panel models.

Enjoy the challenges

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #9
The magnum me-arc advanced remote is not user friendly.  Stick with the std me-rc unless you really want to get into this. It's fairly easy to set up

I have both and have not mounted the advanced remote yet.

"Riding and rejoicing"
Bob
1997 U320 40' Mid entry, build 5132,  wtbi ce27, 4th owner
2007 Solara convertible
2 prodeco tech outlaw ss electric bikes

1095 watts solar
08 Ls 460 and a sc430
2000 Ford F-250 superduty 4x4

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #10
First of all, let me offer my gratitude for everyone who has responded.  There is some really good advice in here.  Based on the information, and the fact that I'm an individual who prefers to prepare first, I have decided to delay even installing the new AGM batteries until I get this situation figured out.

As a result of the fabulous comments, I began to do some more research, and ran across this thread online as a result of the comment about the Magnum Energy MSH3012M.  That in turn led me to further research, and I discovered this video about a Victron Energy device:

Running an RV AC off Solar, Batteries, and a Hybrid Boosting Inverter |...

This video demonstrates closer to what I'm looking for.  My RV is parked in my driveway, and I will be using it both as a traditional RV, driving to many states in America, and also living in it for short periods while I rehab my home.  Sometimes I'll be living in the home, and sometimes the power will be off, and I'll be living in the RV.  That means shore power, probably from a 30 amp circuit.  Finally, during 2019, I would like to try to install solar on the RV because 2019 is the last year you can get a full 30% discount on your federal taxes for it.  Thus, the potential for three or four charging sources - alternator, generator, solar, and short.

Since I need to plan and do this right, I guess my next question is this:  Since my needs are more clearly defined now, who has experience with Victron Energy, and would they recommend the products?

Thanks again everyone!  I love this forum!

Mark
1994 U280 Grandvilla, 40ft.
League CIty TX
Newbie :-)

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #11
You gain a lot with the ME-ARC over the ME-RC.  If you ever want to use a Battery Management Kit (BMK) or an Auto Generator Start (AGS-N), you'll only have partial functionality with the ME-RC.  Knowing your battery State of Charge (SOC), for instance, is a nice feature that I think is only available on the ARC.

http://energyplus.co.tz/NEW/Magnum-Remote-Comparison-Rev1-0.pdf

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #12
I have a 95 also which has the same inverter. My inverter crapped out and i had to decide what to do. I chose to rebuild it. A marine electronics place in sarasota fl convinced me that cost wise it was the best option. I carefully removed it , took it to him and for a resonable price he rebuilt it . It works perfect. Like any inverter you need to make sure you are are not over charging so you dont cook your batteries. Inverters arent cheep and for me this was an easy decision. As long as your inverter doesnt over charge you should be ok. But as you stated its almost 25 years old. Good luck
1995 U320 40', 2013 chevy sonic toad, my real love are corvettes have owned 30

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #13
If you decide to install a solar system, you may not need an inverter/charger.

I have 1400 watts of solar panels, an Outback 80 amp solar controller, an 1800 watt "pure sign" Xantrex inverter and a 50 amp IOTA converter.  Because the solar system reliably keeps my three 8D AGM batteries charged when the sun is shining, and the IOTA (dual voltage) inverter keeps my batteries charged when there is no sun, I would never use a high amperage charger.

I chose an 1800 watt inverter because it can provide 15 amps at 120 VAC which is the maximum for any appliance you may use, while limiting the inverter supply amperage to 180 amps, and costing a fraction of the cost of a larger inverter/charger. I must be careful when using two or more appliances simultaneously to not overload the inverter (ie a microwave and coffee maker). 

I can and do use the inverter and the converter at the same time which cannot be done with an inverter/charger.

The total cost of the solar controller, the inverter, and the converter was half what a 2500 watt inverter/charger was.

By the way, I have only one battery bank not two.

If you plan on recharging batteries with the generator when dry camping, you definitely need an inverter/charger.
Wyatt
96 U320 40 WTFE, build 4943
84 Toyota Supra towd
2015 Jeep Wrangler towd
Victoria, BC, Canada

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #14
Just so there is no confusion, I must elaborate on reply 12 where the poster referenced " the inverter charging the batteries".

An inverter/charger has two functions, firstly, inverting (providing 120 VAC power from 12 volt batteries) and secondly, providing battery charging from 120 VAC (shore or generator).

My Xantrex inverter cannot charge batteries, it dischargers batteries to provide 120 VAC.

My IOTA converter can charge batteries using 120 VAC power.
Wyatt
96 U320 40 WTFE, build 4943
84 Toyota Supra towd
2015 Jeep Wrangler towd
Victoria, BC, Canada

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #15
I have posted this many times.  The Victron inverter/chargers are not NRTL or UL approved. 

My progressive rv insurance policy specifically states that any appliance must be approved by either source. 

Please use marine 1427 UL approved cabling as its pvc cover is fire retardant. 

Std battery cabling rubber cover burns
"Riding and rejoicing"
Bob
1997 U320 40' Mid entry, build 5132,  wtbi ce27, 4th owner
2007 Solara convertible
2 prodeco tech outlaw ss electric bikes

1095 watts solar
08 Ls 460 and a sc430
2000 Ford F-250 superduty 4x4

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #16
Bob

Victon complies with EN 60335-1 (equivalent to UL60335-1)which is recognized by US code agencies via a reciprocity agreement. This is how manufacturers go to market in multiple counties without testing being required in each country.

Here is UL 60335-1 link:

UL - 60335-1 Safety of Household and Similar Appliances, Part 1: General...

Here is a link to main EN60335-1 documents which is reciprocal to UL60335-1

EN 60335 | EUROPEAN INNOVATION PARTNERSHIP

Here is Victron Product spec listing EN 60335-1 certification here:

http://www.victronenergy.com/upload/documents/Datasheet-Multiplus-inverter-charger_2kVA-and-3kVA-120V-US-EN.pdf

So effectively, the Victron inverter is "UL approved" via EN60335-1 Certification

I sell products manufactured in the US that meet US electrical code requirements for UL listing through similar reciprocity agreements.

So whoever is giving you this information is likely mis-informed at best or disingenuous at worst.

I have learned in my distribution business that no large distributor will sell any electrical device without requiring appropriate certifications and manufacturer liability insurance. Too much liability to their business otherwise.

Your insurance company will accept EN60335-1 certification in lieu of UL60335-1 certification. Let us know if you get documentation to the countrary from your insurance company, I am likely subject to a similar requirement in my policy, and I do have the 3000W Victron inverter installed already, and that would be disturbing.

There may be other reasons not to like Victron products, but safety testing and required certifications should not deter anyone from buying Victron.
Tim Fiedler    2025 LTV Unity MBL on Order
2000 Chevy Tracker 2 Door Convertible 4WD Now lifted 4.5"
1985 Citroen 2CV6 Charleston
Murphy Rebel on wheels with 175HP Titan
Cessna P337
1980 48' Westport MY (!/4 Share)

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #17
I also have ALL Victron equipment installed on my coach.. Works great and easily communicates with each of the pieces. I am very happy with it and would do it again if needed.

Great products and if you decide to use Victron which many of us have.. Use BayMarinesupply.com He helped most of us with ourp urchases ..Allen is his name

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #18
Bob

Victon complies with EN 60335-1 (equivalent to UL60335-1)which is recognized by US code agencies via a reciprocity agreement. This is how manufacturers go to market in multiple counties without testing being required in each country.

Here is UL 60335-1 link:

UL - 60335-1 Safety of Household and Similar Appliances, Part 1: General...

Here is a link to main EN60335-1 documents which is reciprocal to UL60335-1

EN 60335 | EUROPEAN INNOVATION PARTNERSHIP

Here is Victron Product spec listing EN 60335-1 certification here:

http://www.victronenergy.com/upload/documents/Datasheet-Multiplus-inverter-charger_2kVA-and-3kVA-120V-US-EN.pdf

So effectively, the Victron inverter is "UL approved" via EN60335-1 Certification

I sell products manufactured in the US that meet US electrical code requirements for UL listing through similar reciprocity agreements.

So whoever is giving you this information is likely mis-informed at best or disingenuous at worst.

I have learned in my distribution business that no large distributor will sell any electrical device without requiring appropriate certifications and manufacturer liability insurance. Too much liability to their business otherwise.

Your insurance company will accept EN60335-1 certification in lieu of UL60335-1 certification. Let us know if you get documentation to the countrary from your insurance company, I am likely subject to a similar requirement in my policy, and I do have the 3000W Victron inverter installed already, and that would be disturbing.

There may be other reasons not to like Victron products, but safety testing and required certifications should not deter anyone from buying Victron.


I hope this settles that topic for the future of discussions.. Sometimes it just sounds like someone wasnt happy with their purchases so they talk the other company down.. Not sure why it keeps getting repeated.. I guess if you say it enough times its believable?

Carry on!!


No matter what brand you decide you really cant go wrong.. some prefer other brands for other reasons.

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #19
Your best bet in a Foretravel, is the Magnum Pro-Sine inverter with Gell batteries.
I had a Heart Interface, but that older technology, also the warranty of 3 years on the Magnum,
and customer service outweighs anything out there.  I talk of many years experience.
Happy New Year to All from Canada,
Alexander
1997 Foretravel U295, updated at Foretravel 2010
Towing - Lincoln MKZ 2013 from new - Excellent
Calgary in the Rockies


Re: Heart Interface 2500 - Keep it? Replace it?

Reply #21
First of all, let me offer my gratitude for everyone who has responded.  There is some really good advice in here.
 As a result of the fabulous comments, I began to do some more research, and ran across this thread online as a result of the comment about the Magnum Energy MSH3012M.  That in turn led me to further research, and I discovered this video about a Victron Energy device:

Running an RV AC off Solar, Batteries, and a Hybrid Boosting Inverter |...

Since I need to plan and do this right, I guess my next question is this:  Since my needs are more clearly defined now, who has experience with Victron Energy, and would they recommend the products?

Thanks again everyone!  I love this forum!
Mark

Mark;  give this guy a call.  He does lots of solar installs and can help you out!  His name is Brian Boone and he also has a facebook page to ask questions, but I would give him a call.  Very knowledgeable!  There is lots of information on YouTube from very knowledgeable folks that are using Victrons as well as Magnum products.  The Hybrid is new technology and yes, can run an A/C if set up right!
  RV BOONDOCKING WITH SOLAR

Joe & Dottie Allen
Sold!  December 2023.      2000 U320; build # 5645
Our coach " Maxine"
Motorcade #  15922;  Escapee 150950; FMCA F330833; Boondockers Welcome;  Harvest Hosts;  Thousand Trails
'98 U320 from 2000-'06
USAF '62-'66

"Do not spoil what you have by desiring what you have not; remember that what you now have was once among the things you only hoped for." ―Epicurus

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #22
I also have ALL Victron equipment installed on my coach.. Works great and easily communicates with each of the pieces. I am very happy with it and would do it again if needed.

Great products and if you decide to use Victron which many of us have.. Use BayMarinesupply.com He helped most of us with ourp urchases ..Allen is his name

Exactly as stated.
Victron system works great
Allen at Bay marine is the BEST!
1995 U320C SE 40'
Jeep 4x4 Commander - Limited - Hemi
"The Pack"  Yogi and Diesel our Airedales -  Charlie our Boxer/Akita mix. Gone but NEVER forgotten Jake our yellow Lab.
NRA Law Enforcement Firearms instructor - Handgun/shotgun
Regional Firearms instructor for national Armored Transp. Co.

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #23
Victron 3k hybrid is my plan. Cheap - no, versital and flexible - yes. Hopefully I can run one roof AC on the road without the generator using solar and alternator and some battery. 50 amp sites all taken, use a 30 amp site. My new Mach 3 PS front ac is only 1200/1320 watts at ARI/desert conditions vs my old rear ac unit at 1600/1930 watts. Replace the new condenser/evaporator fan motor with an ecm motor and drop another 100-150 watts per unit. Can a 13,500 btuh AC unit be built that uses less than 900 watts, the answer is yes, just needs bigger condenser coil. Can that roof real estate taken up by the roof AC units be covered by a removable for service or hinged solar panel, why not.
Old Phart Phred, EIEIO
89 GV ored 36' #3405 300 hp cat 3208 ATAAC side radiator, mountain tamer exhaust brake

Re: Heart Interface 2500 - Keep it? Replace it?

Reply #24
Victron 3k hybrid is my plan. Cheap - no, versital and flexible - yes. Hopefully I can run one roof AC on the road without the generator using solar and alternator and some battery. 50 amp sites all taken, use a 30 amp site. My new Mach 3 PS front ac is only 1200/1320 watts at ARI/desert conditions vs my old rear ac unit at 1600/1930 watts. Replace the new condenser/evaporator fan motor with an ecm motor and drop another 100-150 watts per unit. Can a 13,500 btuh AC unit be built that uses less than 900 watts, the answer is yes, just needs bigger condenser coil. Can that roof real estate taken up by the roof AC units be covered by a removable for service or hinged solar panel, why not.
Have the victron 3000 and a micro air on front ac. Have run it for 10 minutes on just batteries. But SOC was falling pretty quick.  Need to run down the road with alternator charging batteries and good solar, to find out if it feasible.