I am able to use two gfci campground 30 amp receptacles (or 30amp + 15amp) simultaneously because I ran a second neutral wire to the service bay and installed two 30 amp twist lock receptacles in the service bay. I seldom visit campgrounds with 50 amp (really 100 amp) service, so seldom use the 50 amp power cord.
To facilitate using two campground gfci receptacles required rewiring the main power panel in my Foretravel such that the neutral wires from each of the two 50 amp main breakers are connected to separate neutral bars. These two neutral bars are each connected to one of the 30 amp twist lock receptacles in the service bay. A switch on the front of the main power panel allows connecting the two neutral bars together when using the 50 amp power cord.