—-UPDATE—- Power tech generator problem

Had the coach out this weekend and had a problem with the generator.. after about 3 hours of run time it dies and the fault light on the dash comes on. The first time it happened we were about 20 mins from our destination with no good place to pull over so I didn't check it till after we parked. Pushed the fan circuit breaker and the main on off on the panel and it started so I hoped it was a fluke. Today we had stopped for lunch and when we came out the generator was off, the coach was still cool so I don't think it had been off long, it had been running about 3 hours. I moved the same buttons I moved Friday and it started and ran long enough to get the hood closed and get to the door.. trying the same switch moves were not successful in a restart. 2 hours later Stopped at loves to fill up before getting home I tried a restart.pushed the cooling fan reset did not clear the fault light on the dash but turning the main switch off then back on cleared the dash fault light and allowed the generator to start. No lights were on on the generator panel and the power circuit breakers were not tripped.....  Anyone had an issue like this or have an idea where to start looking. The timing is perfect, we are leaving for angel Fire New Mexico Friday and really need the generator for the roof air for the road side stop over the 1st nite.... Texas is HOT right now!
My generator is a power tech 10kw generator

UPDATE.  I THINK WE FOUND MY PROBLEM. With the great help of Rudy we determined that the thermostat was not opening enough and it would shut down on high temperature. The high temp light must not work. Pulled the thermostat ran for 1 1/2 hours no problem.. installed a new thermostat tonight ran for 45 mins with no problem, so with my fingers crossed I hope there will be no more updates.. we'll find out Friday when we leave for New Mexico.. a big thank you to Rudy for being the parts runner while I had to work and the help troubleshooting the problem.....



Keith
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.

Re: Power tech generator problem

Reply #1
Keith,
Did it have a low oil pressure light or over temp light on.  When it cooled down did you check the coolant and the oil level?  It could simply be low on coolant or oil.  I had an issue when I bought my coach 7 years ago it would shut off after about 30 minutes.  What I found was a loose fan belt.  I would check the simple stuff first.
Jerry & Nanci
1999 U270 34'WTFI
2011 Malibu
A smart man knows what to say, a wise man knows when to say it.

Re: Power tech generator problem

Reply #2
Keith- I just went through something like this with my Powertech 10kw.  First I changed fuel filters, then checked coolant and burped the remote radiator.  Still had off and on run, then stop like you. Called Powertech who said they think I have a diesel problem with the Kubota.  Took it to a diesel shop and after looking over everything, we concluded something electrical is sometimes telling the fuel solenoid to shut off and stop the engine.  We replaced the oil pressure switch ( single pole on my Kubota) and the fuel pressure solenoid.  The tech also showed me how I can run the generator on manual by taking out the fuel pressure solenoid, installing a plug in the hole and then using the manual shut off when I am done.  This was a few days ago and so far have not used the generator much but tested it several times over a couple of days before leaving the area in Minnesota.  I had no fault lights on the generator but I am told that is not unusual.

Check out my post titles- a view of the future in the discussion section.  Hope this helps you out and you get it running right.
Ted & Karen
2001 U270 36' - sold after 12 years full timing

Re: Power tech generator problem

Reply #3
Just went out to check some things over. Took off radiator cap, water there. In July changed oil, oil filter and fuel filters. Just got it out of the shop, exhaust pipe had broken off exhaust manifold, fixed. Had them replace fan belt, it was the same size I was there when they replaced it. Just ran it both hoses to and from the radiator are warm so I think there is a water flow.. Did not see a way to burp the radiator, but there is a line from the top of the water pump that ties into the filler neck that I assume would let any trapped air out of the system, it was hot. The fan was running.. The only thing I noticed that was kinda weird was the outer end cap of the radiator was only hot a little more than half way up, water goes out that side at the bottom, the hose going in the top on the other side was hot...  I checked the oil prior to going.. where was the oil pressure switch and fuel pressure solenoid located?
One of my problems is I'm working 430am to 430pm this week so taking it anywhere is a problem.. I have a friend that has volunteered to be a parts runner if I need one..


Keith
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.

Re: Power tech generator problem

Reply #4
Keith- on mine oil pressure switch is just above the oil filter- single pole with a wire attached to it.
Fuel pressure solenoid is up and to the left side - you will see a wire group connected into it.  It is removed with an Allen wrench and fits in left to right.  Take off the cover to check your oil and you can see all this right in front of you.  It is storming and dark here in N. Dakota right now so I can't get a pic.  Best of luck.  Got these parts from a Kubota dealer- fyi.
Ted & Karen
2001 U270 36' - sold after 12 years full timing

Re: Power tech generator problem

Reply #5
Keith,  Which engine do you have the kubota or the Isuzu?

Mine is Isuzu.  The oil pressure sensor is on the back side of Engine.

Drop the pan under the frame and slide the generator out.  it is just left of center, 2/3 from the bottom.  Mine has a single wire on it.

I changed mine out this past spring.  It was leaking oil, the pan caught much of it , which dumped right where I needed to lay while changing.  Fun
1998 U320 40'
2005 GMC Yukon
MC# 17609


Re: Power tech generator problem

Reply #7
Keith, Have your fuel lines been replaced? We had a similar symptom that was due to air getting into the original fuel lines, causing the engine to stall. It would (usually) restart after turning the power toggle switch off/on. Replacing the fuel lines corrected the problem. 
Greg & Cathy
2000 U320 4010 DGFE Build #5650
Had: 1999 Tradewinds 7370

Re: Power tech generator problem

Reply #8
Kubota motor

2002 Is a Different set up than my 2000

Fuel lines are original, MisterEd would it run for 3 hours before this happened?
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.

Re: Power tech generator problem

Reply #9
Hope these pics post
Ted & Karen
2001 U270 36' - sold after 12 years full timing

Re: Power tech generator problem

Reply #10
Perfect!
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.

Re: Power tech generator problem

Reply #11
Kubota motor

Fuel lines are original, MisterEd would it run for 3 hours before this happened?
We have the same generator. Ours was sucking air though tiny cracks in the aged supply lines. Sometimes it would run for 2-3 hours, with an occasional hiccup....other times, not so long. On our generators, turning off/on the master switch on the unit resets the fault code, and primes the fuel system, and purges air through the return to tank line. When the lines get really bad I doubt this would still work.
Greg & Cathy
2000 U320 4010 DGFE Build #5650
Had: 1999 Tradewinds 7370

Re: —-UPDATE—- Power tech generator problem

Reply #12
UPDATE.  I THINK WE FOUND MY PROBLEM. With the great help of Rudy we determined that the thermostat was not opening enough and it would shut down on high temperature. The high temp shutdown light must not work. It was running about 220* Pulled the thermostat ran for 1 1/2 hours at a temp of 180*,no problem.. installed a new thermostat tonight ran for 45 mins with no problem at 177*, so with my fingers crossed I hope there will be no more updates.. we'll find out Friday when we leave for New Mexico.. a big thank you to Rudy for being the parts runner while I had to work and the help troubleshooting the problem.....
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.

Re: —-UPDATE—- Power tech generator problem

Reply #13
If you have a source and part number for the thermostat,please post,thanks.
96 U270 BUILD 4810
85 380SL
Drummonds TN.

Re: —-UPDATE—- Power tech generator problem

Reply #14
After I changed out my fuel lines I had a hard time getting it started. Worked to much to worry about it for a while, but then just tried to restart it many times, after bleeding the fuel lines and it started, rough at first, but then all was good, for a bit, then it cut out.
Going to change to oil soon, and the air filter, and coolant on it (Isuzu Engine) and fuel filters, and see. If  still having issues with it will try changing out the solenoid and oil pressure sensor and thermostat. In fact, if they are not to expensive, I think I will order double to have on hand.
If anyone has the part numbers for the Isuzu for those that would be great.
Searching these forums can be hard sometimes for those. Tried to find the part number for the air filter on it and couldn't.
Sucks when the genny doesn't work.....

Also HDFF, thanks for posting the resolution to your issue.
 There are so many dead threads here of people not finishing their issue and the resolution of how it came to be fixed to be a real annoyance. You have to search a lot of dead threads sometimes to find the winner. And while Barry's excellent resource has a ton of info, doesn't always have what I was looking for.
'99 U320 40 WTFE
Build #5462,
1500 Watts Solar 600 amp Victron lithium
2012 Jeep Grand Cherokee Overland Hemi
Instagram bobfnbw
Retired

Re: —-UPDATE—- Power tech generator problem

Reply #15
Changing out any diesel fuel supply line introduces a lot of air to the system. With the generator, you can open the little valve with the "T" handle if you have one and then just go to the glow position on the toggle switch at the generator or supply 12V to the electric fuel pump and pump for about 30 seconds. If you don't have the bleed valve that allows fuel and air to go back to the tank, you will have to open a low pressure fuel line at the injection pump. Why? Because the electric pump does not have enough pressure to overcome the spring loaded return valve that requires somewhere around 7 psi to overcome the spring's pressure. Photos below show the 4 psi the electric pump generates and the return valve. If you don't have a return valve, you can just loosen the nut next to the location of the check valve and get rid of all the air that way. If you try and start the engine before you bleed the system, you may get air into the main injection pump. This may require at least one line to be loosened a half turn at the fuel injector and then the engine cranked until it starts.

Pierce
Pierce and Gaylie Stewart
'93 U300/36 WTBI
Detroit 6V-92TA Jake
1140 watts on the roof
SBFD (ret)


Re: —-UPDATE—- Power tech generator problem

Reply #17
I did an r&r on my Kubota cooling system last year. I replaced the thermostat, hoses, water pump and had the radiator cleaned. Its kind of funny I was going to just buy a new radiator. Theyre so small they cant cost much. Well I went shopping and found that they cost over $1500!!! Make darn sure you take care of it. It cost me $70 to get it cleaned.
92 Grand Villa
Silver 6v92
 side isle.
build# 3973

Re: —-UPDATE—- Power tech generator problem

Reply #18
I did an r&r on my Kubota cooling system last year. I replaced the thermostat, hoses, water pump and had the radiator cleaned. Its kind of funny I was going to just buy a new radiator. Theyre so small they cant cost much. Well I went shopping and found that they cost over $1500!!! Make darn sure you take care of it. It cost me $70 to get it cleaned.

In 2015 when we were preparing to move south, we needed to have the radiator in the Rockwood repaired and since the radiator shop was amenable I have my eBay find for my motorcycle cleaned and tested.  While I was in and out, the guy was working on a four section radiator for a Volvo generating plant that ran the rock crusher in a gravel pit.  The lead time for the Volvo radiators was way out there, and as it turned out it was less expensive and faster to build a new radiator array.

When the manufacturer quotes a fantasy price, keep in mind that it's just a radiator and there are people who still make a living repairing and building radiators.  And the cost may be more reasonable than you would think.

Home - Bob Rondeau's Radiator Shop
1992 Foretravel Grand Villa
U225 SBID Build No. 4134
1986 Rockwood Driftwood
1968 S.I.A.T.A. Spring
1962 Studebaker Lark
1986 Honda VF700C
1983 Honda VF750C
Charlie, the Dog was broken out of jail 24 Oct 2023
N1RPN
AA1OH (H)e who must be obeyed.

Re: —-UPDATE—- Power tech generator problem

Reply #19
I had the radiator cleaned out at A mom and pop old school shop, the old guy wouldn't take any money. Here is a pic of the thermostat and gasket package, they were around $30. Heading to New Mexico in the morning so hopefully it passes the test.
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.

Re: —-UPDATE—- Power tech generator problem

Reply #20
Well the party is over, Friday the generator ran for 10 hours before shutting down and giving me a fault light on the dash. Rode the last 2 hours with the windows open, not to bad. Reset it this morning and it ran for about 20 minutes and shut down. We are in New Mexico so it's cool enough that I won't need it, gonna be a warm ride home next week.....
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.

Re: —-UPDATE—- Power tech generator problem

Reply #21
Link Sharing

With any luck. The above pictures will show the loose belt put on by ..... Its too large to be tightened any more. This is the 8k isuzu Pt generator. I will do research to find proper belt. The water pump and thermostat part numbers I listed are correct for the 3lb1 engine.
1999 U270 40 #5518
USN. USPS.

Re: —-UPDATE—- Power tech generator problem

Reply #22
Do you have a fault light on the generator panel?
previous 1984 35 ft ORED 250 HP 3208 Cat       
previous 1998 40 ft U295 CAI 325 hp Cummins
previous 2003 40 Ft u320 build #6140 450 Cummins M11.                                                         
1999 Mazda Miata
Ron, Nancy, Tipper the cat, Max The dog
1997 U 270 36 ft build number 5174 8.3 Cummins

Re: —-UPDATE—- Power tech generator problem

Reply #23
Well the party is over, Friday the generator ran for 10 hours before shutting down and giving me a fault light on the dash. Rode the last 2 hours with the windows open, not to bad. Reset it this morning and it ran for about 20 minutes and shut down. We are in New Mexico so it's cool enough that I won't need it, gonna be a warm ride home next week.....
Have you metered out the latching relay ? I had a flaky genset a few years back and it was a bad latching relay. It would loose contact and shut the generator down.

Mark
The selected media item is not currently available.
Mark and Tanya
Milton , Florida
US Navy Veteran (DV)
1999 U270 Special 40' CAI , 2015 Jeep Wrangler Sahara

Re: —-UPDATE—- Power tech generator problem

Reply #24
No lights on the Ginny are on, just a red fault light on the dash.

Where is this latching located? Do you have a power tech 10k?
The selected media item is not currently available.Keith & Jo
2003 U320T 4025 PBBS Designer series
Build 6203    Cummins 500hp
2000 U320 4010 WTFE / Build 5762 —Sold—
Motorcade #18070   
Pasadena, Texas
2015 Jeep Wrangler Sahara-Sunset Orange pearl coat
Don't argue with a fool, people watching might not be able to tell the difference.