Gas connection to a large propane tank
Have a U270 and a "extend-a-stay at the Onboard tank where the gas grill connector is. Have a large propane tank 40 ft from that the onboard "extend-a-stay" which allows the propane distributor to deliver bulk propane to keep the coach warm in the winter. (They will not fill the onboard tank)
PROBLEM: the two stage regulator on the coach freezes up when the furnace is operated (it does not freeze if the onboard tank is used) which means the gas in the pipe to the regulator is liquid and not vaporizing posing a serious danger.
NO: the bulk tank is not over filled, checked and rechecked it's at 60%
Has anyone else used a bulk tank?
-There is no regulator on the bulk tank.
AM I RIGHT? This is what is required:
1) the two stage regulator needs to be replaced with a low pressure (approx 11" Lb) regulator.
2) A 10 Lb regulator should be installed on the pipe exiting the in board tank.
3) A T-connector between the two regulators on the coach to connect the bulk tank to the coach.
4) A 10 lb regular on the pipe from the bulk tank before it enters the coach.
My propane supplier has had a few crazy suggestions, any of you out there who have had this issue, I have used an extend a stay and never had an issue before.
David