Topic: Generator problem (Read 347 times) previous topic - next topic

Generator problem

I changed the oil and the oil filter and air filter in my generator 6500 LP. Can I start the generator when I'm plugged into ShorePower? I unplugged shore power got the generator started but I have no power to the coach?? I see a little arrow about a breaker on the side of the generator engine but now I can't get the generator to start to test it. It worked fine before I just wanted to change the fluids because they were due but now there is a problem.
Michael & Roxene, Aussie the wonder dog & his daughter Luna the lunatic.
1993 Grand Villa Unihome 280 build #4203
36' 8.3 Cummins 300 hp- 2001 Chevrolet Tracker toad

Re: Generator problem

Reply #1
1. Can I start the generator when I'm plugged into ShorePower?
2.I unplugged shore power got the generator started but I have no power to the coach??
3.I see a little arrow about a breaker on the side of the generator engine
3a. but now I can't get the generator to start to test it.

Michael,

1.Yes if the transfer switch is working correctly
2. This could be the transfer switch not swapping from shore to generator.
3. You can turn the breaker off and back on to make sure that it  is not tripped
3a.  Check and clean the battery cable  ends and the ground cable ends.
3b. Check the oil pressure switch to see if the wire is loose.
3c.  You did get it full of oil and double checked

Mike
Pamela & Mike 97 U 320

"It's not what happens to you, but how you react to it that matters."

Re: Generator problem

Reply #2
Mike, thanks for the tips, it was the breaker on the side of the generator, everything is working good.
Michael & Roxene, Aussie the wonder dog & his daughter Luna the lunatic.