Topic: Surging AC when on the generator (Read 730 times) previous topic - next topic

Surging AC when on the generator

I just have to wonder why our front ac surges when using it on generator power. 
It makes the volt meter wiggle about 5 volts and it's irritating. Makes a surging noise.
  Still puts out cool air.
  Still runs fine on shore power.
  The bedroom ac isn't doing the same thing.
 
At first I thought it was the generator doing the surging but outside the geny sounds just fine. As soon as I turn off the front ac everything is smooth as silk. 

 Has anyone else had this issue and what was the fix. 
Robert and Susan
 1995 36' 280 WTBI 8.3 3060r
 1200 watts on the roof, 720 Ah of lithium's
 Build # 4637. Motorcade # 17599
        FMCA  # 451505
        18  Wrangler JLUR

Re: Surging AC when on the generator

Reply #1
Think I would start with the wire nut connections where the air conditioner wiring connects to the house wiring.
John Duld
1995 U320C SE 40'

Re: Surging AC when on the generator

Reply #2
Thanks John. I'll check that out.  Are those accessed from the top or bottom ?
Robert and Susan
 1995 36' 280 WTBI 8.3 3060r
 1200 watts on the roof, 720 Ah of lithium's
 Build # 4637. Motorcade # 17599
        FMCA  # 451505
        18  Wrangler JLUR

Re: Surging AC when on the generator

Reply #3
The connections are accessible from below. Remove the filter and look towards the front of the opening and see a metal electrical box with metal lid remove the lid or cover and the wires are inside.
previous 1984 35 ft ORED 250 HP 3208 Cat       
previous 1998 40 ft U295 CAI 325 hp Cummins
previous 2003 40 Ft u320 build #6140 450 Cummins M11.                                                         
1999 Mazda Miata
Ron, Nancy, Tipper the cat, Max The dog
1997 U 270 36 ft build number 5174 8.3 Cummins

Re: Surging AC when on the generator

Reply #4
If you have the front unit on and rear off is it still surging?  If the voltage is also surging I would say it is the generator when it has that load on it.  Possible fuel filter needs to be changed. 

Do you have a Hz meter to see if generator is putting out 60 Hz. and staying at 60 Hz?
2014 ih45  (4th Foretravel owned)
 1997 36' U295 Sold in 2020, owned for 19 years
  U240 36' Sold to insurance company after melting in garage fire
    33' Foretravel on Dodge Chassis  Sold very long time ago

Re: Surging AC when on the generator

Reply #5
I second what turbo jack says. I had the same issue before and it was the fuel filter. I believe your problem to be fuel related. It's just not getting enough fuel supply.