Catastrophic fuse size

OK, I intend to have 200W solar panel output on the roof of the coach at 26V this spring. Just enough to keep the batteries charged I hope.
Should I install catastrophic fuses? What size. if any?
Nitehawk,  Demolition Lady, & our NEW master, Zippy the speeding BB cat.
1989 Grand Villa 36' ORED
Oshkosh chassis, 8.2 DD V8
2006 Saturn Vue AWD

Re: Catastrophic fuse size

Reply #1
I'd say 30 or 40 amp -- 1 on the hot line between the panels and your solar controller and one between the controller and the batteries. (another between the batteries and the inverter if you connect one)
1993 U225 Build #: 4285
500 Watts Solar
Honda CRV AWD
Former 1981 Foretravel Travco
Retired, Full Time Off Grid Snowbird

Re: Catastrophic fuse size

Reply #2
I installed a 250 amp fusible link down where the solar goes into the battery connection at the electrical bus. I also have breakers up where the solar goes into and also out of the controller. You can't be too safe when a lot of amps are available. Northern Arizona Sun and Wind and Midnite tech recommended this.

Arrows point to the fusible link.

Pierce
Pierce and Gaylie Stewart
'93 U300/36 WTBI
Detroit 6V-92TA Jake
1140 watts on the roof
SBFD (ret)

Re: Catastrophic fuse size

Reply #3
Volts times  Amps equals Watts, Watts divided by voltage equals amps. 200w divided by 12v equals 16.67 amps. 25 amp fuse would protect. I think solar panels can be shorted out (please double check) and not be damaged.
Scott

is it ok to short circuit a solar panel - Google Search

No - you will not damage a solar panel by shorting it. Solar panels are designed to be continuously operated at very very close to their short circuit current. A good quick test of a solar panel is to run it short circuited into an ammeter.

is it ok to open circuit a solar panel - Google Search

Yes. It does not hurt them to be disconnected—open circuited. Leaving anything out in the sun and rain will cause eventual degradation.

Re: Catastrophic fuse size

Reply #4
Trying to amplify Mr. Davidson's remarks, a circuit breaker can carry continuously about 75% of its rated current.  That being said, for protection multiply your maximum current by 1-1/3 and choose accordingly.
1992 Foretravel Grand Villa