Re: 50amp RV power conversion to 220v household
Reply #15 –
IN REPLY #4 OldManSax said" every coach I have owned, that came with 50A service from the factory, had 220V to the breaker panel WHEN PLUGGED INTO A 50A PEDESTAL. A lot of coaches, including mine, have 220V when running the generator."
I agree that some (not all) 50A Pedestals have 240 volt and provide 240v to the breaker panel, however, I doubt that the generator in a Wonderlodge is wired to provide 240v to the breaker panel. I have not seen a Foretravel which has 240v to the breaker panel. My Powertech 10K generator in my 1996 Foretravel has the output wires from the two 120v armatures shorted together at the generator such that each armature provides exactly half of the amps required while the voltage control is only on one of the armatures. The uncontrolled armature will output the same voltage as the controlled armature because the amps are identical. The two hot wires (one black & one red) from the shorted armature output wires to the breaker panel will NOT carry the same current, while the neutral wire (white) from shunt to panel carries the sum of the amps of the two hots (ie the full generator output).
Question to OldManSax: Have you actually measured 240v at your breaker panel when powered by the generator? If you have, I am very curious as to how your generator provides both 240v and 120v to the breaker panel (ie switching circuitry or a transformer at the breaker panel).