Re: Aquahot controller technical question
Reply #1 –
The Control Unit that runs the burner looks at the voltage from the flame sensor to determine there is a fire. When the incoming voltage to the burner gets below 11.5, it is easy for the flame sensor voltage to go below 10 volts. The control unit will determine the flame is not sustainable at voltages below 10 volts. The control unit then faults, turns off the fuel, cools for 3 minutes and stops the burner till someone turns the burner off and back on to remove the fault.
Newer heaters have an electronic control board to run the heater. It has a low voltage light that will stop the burner during low voltage conditions. A micro switch must be pushed to turn the low voltage light off to restore operation.