Re: A/C operation
Reply #5 –
Since you don't mention any circuit breakers tripping, I will assume that your A/C units are shutting down due to seeing low voltage/amperage on their power supply.
I'm not by any definition an electrical expert, but my armchair guess is that your 8 kW generator should be able to handle 2 A/C units, ASSUMING that it is putting out the advertised rated power. I think you would need a digital multimeter with a clamp-on ammeter to check the generator output.
About the soft start question. We have a Micro-Air EasyStart on our residential 4-ton heat pump. It reduced the LRA (lock rotor amps) from 109A to 30A. The LRA is the big spike in amps (inrush current) that happens when the compressor motor turns on. It only lasts for a few milliseconds, and then the compressor settles down to its running amp draw which is a lot lower.
SO, if your problem is being caused by the LRA spike from the second A/C overloading the generator, then a soft start might help.