Re: Voltage problem revisited
Reply #4 –
Yes, if you are safe working around 120/240 VAC, open the ATS. If two open the one with generator and shore IN and OUT to main breaker panel (the one to the main breaker box is short and easy to trace).
Check for power IN and OUT
On 50 amp shore power:
Black to white= 120 VAC
Red to white= 120 VAC
Black to green= 120 VAC
Red to green= 120 VAC
Green to white= 0 VAC
Red to black= 240 VAC
On 30 amps-- all the same except red to black= 0 VAC
If you don't get those readings on the IN side, work back toward shore power cord until you find the culprit.
On the shore power cord:
Two outer straights= hot
Center straight= neutral
Center round= ground