Re: Solar project. What am I forgetting. What would you change?
Reply #11 –
I use the same Midnite Solar "baby box" with dc breakers, which also doubles being your disconnects between solar panels positive lead and the Victron solar contoler too. Be sure you mount the Midnite dc breakers in the proper direction, as there is a proper in and out direction of dc from the positive panel lead. I questioned this with an Israeli mfg of these dc breakers, and was told if wired in the wrong direction, this could effect the life and protection capability of the dc breaker. On the inverter side I used a properly sized Blue Sea circuit breaker to cutoff solar charge controller to batteries, similar to the following from Bay Marine on Amazon. Bay Marine can advise you on size for your system.
Bay Marine Supply 187 Series Circuit Breaker â 110A Surface Mount 48V DC Max...
I am glad you are buying the items from Bay Marine, that assures you of getting the right enginered items with the proper quality and support. Many buy the lowest priced wire on the web, and end up with copper covered aluminum wire that has higher resistance. The wire from Bay Marine will be 100% copper, as it should be.
There is a proper connect sequence. First connect to batteries, this powers up the Victron solar controller, then connect solar charge controller to panels. Disconnecting is reversed, first disconnect from solar panels then disconnect solar controllers from batteries. Victron manual should be read carefully for a safe install. It will advise on first connection, and on how to update bios if wi fi is available. Double check that you are connecting to the proper posts on the Victron charge controller, double check for proper proper + and - leads from panels with a volt meter. An error here will destroy your Victron charge controller!